    Kitchen Outlets & AC not working on Generator Power

    I have a 2011 Cyclone model 3010. I am the original owner and bought it brand new. Recently I had an issue where the outlets in the kitchen and the air conditioner would not work when the generator was running, but they work if I am connected to shore power. They worked previously off of the generator, so not sure what is going on. I checked all fuses and circuit breakers and all looks good. I also checked the fuses on the PD9280 charger/converter and they were also fine. Batteries in the unit are brand new. Problem started before I changed the batteries. Any suggestions as to where to look for problems ???

  2. Print this Post   #2
    Moderator danemayer's Avatar
    Join Date
    Jul 2010
    Location
    USA - CO
    Posts
    19,141

    Re: Kitchen Outlets & AC not working on Generator Power

    Sounds like one of your two hot power legs is missing.

    Start with the generator. There are 2 circuit breakers on the front. One of them may have tripped.

    Next thing to check would be the automatic transfer switch. It's usually behind the rear wall of the pass through basement storage.

    Two other possible problem areas: the junction box where the generator wires connect to the wires that go to the transfer switch, and the wires attaching to the back side of the main circuit breaker panel.

    Our Electrical User Guide in this folder has pictures, drawings, and explanations that you may find helpful.


    Dan and Ann Mayer & fur baby Callie the Rally Dog
    2011 Landmark Rushmore
    • MorRyde 8K Independent Suspension
    • 8K Kodiak Disc Brakes
    • RV Comfort Systems Cheap Heat
    • MorRyde 33x90 Sliding Cargo Tray
    • Torklift Glowstep Revolution Aluminum Steps & Dirt Destroyer

    2014 RAM 3500 Laramie
    • Cummins 6.7 Diesel, AISIN Transmission
    • 4x4, Long box, Crew Cab, DRW 3.73
    • Hensley BD3 TrailerSaver Hitch
    • Garmin RV760 GPS


    Is club membership right for you? Click here to learn more

    Check out our Owner-written User Guides and Troubleshooting Guides

  3. Print this Post   #3
    Junior Member
    Join Date
    Jul 2012
    Location
    USA - AZ
    Posts
    2

    Re: Kitchen Outlets & AC not working on Generator Power

    Thanks Danemayer !!! Makes sense and goes along with some thoughts I had. I will check the generator and I am working on removing the panels in the basement to get to all that stuff behind it. Will post what the problem and resolution is if I figure it out !!! Cheers

  4. Print this Post   #4
    Senior Member wdk450's Avatar
    Join Date
    May 2008
    Location
    USA - CA
    Posts
    5,509

    Re: Kitchen Outlets & AC not working on Generator Power

    From the way you described this occurred, I would tend to suspect contacts (circuit breaker switches and relays) over connection problems. Fortunately, this problem is limited to the generator power and power switching system, and therefore there aren't too many places to check. Once you get to the transfer switch the current routing is common with the shorepower, that works. You are probably going to have to take readings with an digital voltmeter, or maybe you could just use a non-contact voltage sniffer on the 2 phase hot wires. Fuses need to be double checked with an ohmmeter, not just a visual check. Circuit breaker contacts can go bad. The biggest thing that I would suspect would be the transfer switch relay contacts, due to possible arc pitting and corrosion. You MAY be able to get this to work with DeOxIt electrical contact cleaner/restorer spray on the relay contacts, or file the contacts with a burnisher or flat swiss file. Best to replace the relay if it is found to be the problem. Be sure to remove ALL voltage sources when working on the transfer switch relay.

    A possible technique to PREVENT transfer switch contact damage is to work it so that when the generator comes on there is no electrical load present. You can do this by turning OFF the inside mains circuit breaker before starting the generator. Once the generator is up and providing voltage through the transfer switch, then turn ON the inside mains breakers. This puts all of the load connection electrical contact arcing on the inside mains breakers that are cheaper than the transfer switch, more accessible and easier to install than the transfer switch, and are available at most any hardware store. I keep an extra inside dual mains breaker on hand. When turning OFF the generator, similarly turning OFF the inside mains breaker while the transfer switch relay switches under NO ELECTRICAL CURRENT LOAD will prevent a similar electrical arc on the transfer switch relay contacts. Then turn the inside mains breakers back ON for shorepower.
    Bill Knight KJ6TBE
    Retired 40 Year Hospital Biomedical Electronics Technician
    Former State Chairman (2000) California Medical Instrumentation Association (CMIA)
    2008 Bighorn 3670RL
    My Bighorn Upgrades
    See:
    https://docs.google.com/document/d/1...it?usp=sharing


    2004 Dodge RAM 3500 Cummins 5.9
    B-D Exhaust Brake
    Ride Rite Air Bags
    Valvoline 15-40 High Mileage Diesel Oil
    XDP Diesel Power Plus Fuel Additive

    At a Thousand Trails in Southern California

    21 Heartland Rallies I Have Attended
    See: https://docs.google.com/document/d/1_PRxlhCp1l7IXgiVIBJmCtX3viJ9NaykR8_b81W9CVU/edit?usp=sharing

    Thousand Trails Elite Membership

    Support this Forum! Join the Heartland Owners Club at the "Owners Club" Tab at the top of this Page!!!
    Remember The USS Liberty . . . Read: http://www.lewrockwell.com/orig/margolis12.html
    "The truth sounds like hate to those who hate the truth"

Similar Threads

  1. Kitchen outlets and hall light not working
    By rosemarieh57 in forum 120 volt AC
    Replies: 4
    Last Post: 02-28-2019, 10:28 AM
  2. electrical plugs not working on generator power
    By heyjude in forum 120 volt AC
    Replies: 5
    Last Post: 05-20-2016, 01:00 PM
  3. GFI outlets not working
    By paul_laplante in forum 120 volt AC
    Replies: 6
    Last Post: 03-23-2015, 07:42 PM
  4. No power kitchen outlets
    By soilmovers in forum 120 volt AC
    Replies: 5
    Last Post: 04-02-2008, 05:39 PM

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •