Bubba, I understand how fustrating things can get when you are working on something that you cannot seem to get right. But your rant against Heartland here almost seems like kicking the dog bacause you had a bad day at work. I am sure we can help you figure out where the problem is and what to do. Here are a few things I can think of to check:
1. Did everything work before you started?
2. What is the battery voltage? A charged battery should be 12.7 volts. What is the voltage at the terminals after the battery is connected?
3. What is the voltage at the disconnect?
4. Seems like the generator is connected to the battery. Is there a splice at the battery terminal that may have come loose?
5. I would chase out the battery voltage in a logical path to find out what may have come loose or disconnected.
6. What is the battery voltage at the converter?
Here is a table of battery charge %
[FONT=Verdana, Arial, Helvetica, sans-serif]
12.65V [/FONT][FONT=Verdana, Arial, Helvetica, sans-serif]
=100%[/FONT]
[FONT=Verdana, Arial, Helvetica, sans-serif]
12.45V[/FONT][FONT=Verdana, Arial, Helvetica, sans-serif]
=75%[/FONT]
[FONT=Verdana, Arial, Helvetica, sans-serif]
12.24V[/FONT][FONT=Verdana, Arial, Helvetica, sans-serif]
=50%[/FONT]
[FONT=Verdana, Arial, Helvetica, sans-serif]
12.06V[/FONT][FONT=Verdana, Arial, Helvetica, sans-serif]
=25%[/FONT]
[FONT=Verdana, Arial, Helvetica, sans-serif]
11.89V or less[/FONT][FONT=Verdana, Arial, Helvetica, sans-serif]
=Discharged[/FONT]
Keep us posted and good luck, John