I was putting my coroplast(underbelly material) back up and I touched the spring hanger and got a shock.
I ran en extension cord out to the spring hanger, and put the negative from my volt meter into the ground of the extension cord and put the positive onto the spring hanger and had 41 VAC.
Had DW turn each breaker off 1 at a time, and the voltage dropped with each breaker turned off.
Any thoughts??
Thanks.
Tom