When this happened on ours just flipped the breaker off for a moment then back on all ok since then.
E7 code from the Dometic web site
Loss of 120 VAC power to all power mod- ule boards on the system. The system will shut down.
Found the problem, A loose wire on the Neutral Bus bar which had a little melt down, cut out the bad section and all is working as it should.
Before you pull the circuit breaker panel, it's a good idea to disconnect shore power.
Hi TacoTom,I have 3 AC's in this Cyclone 3800
Hi TacoTom,
First of all, I've merged your new thread with the earlier one so all the answers are in one place.
Either I missed it or this is the first time you mentioned that you have 3 AC's. Because of power limitations, only 2 can be run at a time. There's a transfer switch that switches power between 2 of the units. The 3rd unit should be able to run all the time.
That leads to 2 questions: 1) does the problem occur when the other AC units are turned off? 2) have you traced the wiring back to the transfer switch. To find out where the AC transfer switch is located, you might need to call Heartland Customer Service at 877-262-8032 / 574-262-8030. Have your VIN # ready. Or perhaps someone else can chime in with the location.
Tom,
You also need to ask them how they wired your unit. I think some units were wired so the living room is always available and the transfer switch powers either the bedroom or the garage. On other units I think they may have set the bedroom to always be available and the switch alternates between living room and garage. I think the wiring setup goes with how you use the trailer. If the garage has bunks that get used all the time, you might want the front bedroom to be primary, and switch between garage and living room. If the garage is an office, you might want the living room primary and switch between bedroom and garage/office.
If you can run both the bedroom and garage units at the same time, one of them is primary and is always available - probably the front bedroom. The other gets power through the transfer switch. And by process of elimination, if you can run both bedroom and garage at the same time, the living room must be powered by the transfer switch and alternates with one of the other units - probably the garage.
So if you can run bedroom and garage at the same time, my guess would be a wiring problem between the transfer switch and living room AC, or a transfer switch failure.
Make sure you're clear with customer service that you're NOT talking about the main transfer switch that alternates between shore power and generator.
I don't think you need to check the other wiring at this point. Once you find the transfer switch, look for the mfg/model info and download the manufacturer's troubleshooting info. There may be some checks you can do (with great care) to determine if it's working correctly.
I would guess there's romex from the circuit breaker box to the input side of the switch, and 2 romex lines from there to the living room and probably the garage AC units. Since one AC unit powered from the switch is working, the input connections are ok. And one set of output connections is ok. With the cover off the unit, being very careful, you can probably use a voltmeter or non-contact voltage tester (better) to determine if the transfer switch is transferring power correctly.
If you share the mfg/model info, I'll post the manuals here on the forum for the next guy.
I will check back with you on Friday as I have to pack up and Travel tomorrow.
I don't think you need to check the other wiring at this point. Once you find the transfer switch, look for the mfg/model info and download the manufacturer's troubleshooting info. There may be some checks you can do (with great care) to determine if it's working correctly.
I would guess there's romex from the circuit breaker box to the input side of the switch, and 2 romex lines from there to the living room and probably the garage AC units. Since one AC unit powered from the switch is working, the input connections are ok. And one set of output connections is ok. With the cover off the unit, being very careful, you can probably use a voltmeter or non-contact voltage tester (better) to determine if the transfer switch is transferring power correctly.
If you share the mfg/model info, I'll post the manuals here on the forum for the next guy.